@Enhineyero: Ref ASCE 7-05 & ACI 318-11. In response to your first post - It is possible to use flat slab + columns (moment-resisting frames only and no shear walls) as LFRS. OMRF( R = 3) is permitted in low seismic risk zones, SDC A and B. IMRF( R = 5) is permitted in low to moderate seismic zones, SDC C and lower. SMRF(R = 8) is permitted in all seismic zones. Seismic detailing requirements of ACI Chapter 21 are required for frame members in SDC B and higher but not for SDC A.
SDC A & B ~ UBC Zones 0 & 1, SDC C ~ Zone 2, and SDC D, E, & F ~ Zones 3 & 4.