Something doesn't add up in section D.5.2 (concrete breakout strength). If I work through the example shown in Figure RD.5.2.3, I actually get a HIGHER capaciy using the hef restriction in section D.5.2.3. Here's what I'm coming up with:
Using limit on hef:
hef = 4 in
ANC = 200 in2
ANCO = 144 in2
Nb = 12.1 kips
psied,N = 0.90
other psi factors = 1
----------------
Ncb = 15.1 kips
Neglecting limit on hef:
hef = 5.5 in
ANC = 223 in2
ANCO = 272 in2
Nb = 19.6 kips
psied,N = 0.85
other psi factors = 1
----------------
Ncb = 13.7 kips
The commentary says that the limit on hef is because the results are too conservative using the full embedment. The above example seems to indicate the opposite. The only thing I can think of is that the new hef should not be used in D-6 (even though the code says that equation is included). Am I missing something here, or is there a "BUST" in the code???
Using limit on hef:
hef = 4 in
ANC = 200 in2
ANCO = 144 in2
Nb = 12.1 kips
psied,N = 0.90
other psi factors = 1
----------------
Ncb = 15.1 kips
Neglecting limit on hef:
hef = 5.5 in
ANC = 223 in2
ANCO = 272 in2
Nb = 19.6 kips
psied,N = 0.85
other psi factors = 1
----------------
Ncb = 13.7 kips
The commentary says that the limit on hef is because the results are too conservative using the full embedment. The above example seems to indicate the opposite. The only thing I can think of is that the new hef should not be used in D-6 (even though the code says that equation is included). Am I missing something here, or is there a "BUST" in the code???