I think we have very different ideas of pomp and circumstance. Only difference is whether or not I put the inspection requirement in a schedule during design and whether or not I send the report to the building official after substantial completion of the structural elements of the building. The inspection itself is materially the same - I even use the same form, just check "routine observation" or "special inspection" at the top.
It appears so. It's definitely a PITA IMO. Have to submit statement of SI, schedule of SI, approved agencies, daily reports, interim reports, final reports - all coord. with the design team, GC, and AHJ. Georgia's SI guide is 35 pages.
Or just conduct your own site visit and call it a day.
Also, be careful what you inspect. In Georgia, a PE is actually pretty limited on what they can inspect for SI. You need a bunch of different certifications to look at different things and a PE doesn't automatically qualify you for everything structural. Not sure about VA.
It still says as approved by the building official. Meaning the final decision is not with the engineer, but with the building official.
Agreed. This is true for everything in construction and the AHJ can require anything they like. They could make you do pushups for a permit if they want!
Jokes aside, the point of my reply was to point out what is required by the EOR to fulfill our duty. Why start out by requiring an extensive SI if you, as the EOR, deem it unnecessary and it's not mandated by the code? If the AHJ disagrees, then they can require it.
So I'm not on board with letting the plan reviewers waive special inspections by negation (or lack thereof).
EOR can require it, but the AHJ can also ignore it.
I get it, though, and have used that method many times in the past. It's only very recently that I'm starting to question whether or not it's a good model to perpetuate.
My logic is I would much rather see it myself the have the GC pocket engineer approve everything they do.
From the 2021 Virginia Residential Code (2018 IRC, edited) as available on iccsafe.org:
View attachment 7480
Thnx for the snip. First sentence is worded so weakly. If they want you to follow the IBC, why not say it's straight up required? Seems up for interpretation as worded. Nonetheless, the exceptions of IBC noted above would still apply if EOR deems appropriate.