IEBC Allowable 5% Gravity Increase on Total Load or Load Type?
waytsh
383
My understanding based on previous editions of the IEBC is that the 5% increase was based on the total gravity load. The wording in the more current versions, however, could be read as 5% of the load type, i.e. dead, live, or snow.
“Any existing gravity load-carrying structural element for which an alteration causes an increase in design dead, live or snow load, including snow drift effects, of more than 5 percent shall be replaced or altered…”
How do you guys read this?
I would consider total load as well.
With roof live loads decreasing to 20 psf from 30 psf, that is an easy location to find some additional SID capacity in renovations...
The existing building code is really poor in it's wording. I find designers have wildly varying interpretations and AHJ's often have a very inadequate enforcement. I think the IBC should include multiple different "example" projects with the correct interpretations.
Yes - you must become one with your inner lawyer when it comes to the IEBC. I'm going to go against the consensus so far and say that my interpretation of the 2021 IEBC is for each load case (not sure I completely agree with that, but that is how it reads). The 2015 IEBC was clear this exception was limited to less than 5% stress increases, not even mentioning individual cases. Why would they diverge from this very clear requirement to this wording unless there was a deliberate change of intent. If their intent was to essentially have the design checks be equivalent between 2015 and 2021, they did a very poor job.
Regardless, I would send an inquiry to ICC and will likely do so myself next time I run into this limitation.
Based only on the text of the quoted passage above, I agree with @Flotsam7018 that the 5% limit is for the magnitude of each load, not the total load or load effect. That is what the text says, but I do not know if that is what was meant. In practice, I would probably stick to 5% total load or load effect.
Sometimes it is necessary to write the total story to get the requirement:
[BS] 706.2 Addition or replacement of roofing or replacement of equipment. Any existing gravity load-carrying structural element for which an alteration causes an increase in design dead, live or snow load, including snow drift effects, of more than 5 percent shall be replaced or altered as needed to carry the gravity loads required by the International Building Code for new structures.
My interpretation is ;
- 706.2 is for Addition or replacement of roofing or replacement of equipment,
- t
- If the alteration causes an increase in dead, live or snow load..of more than 5 percent , replacement or alteration is required if necessary. That is , if the addition or alteration causes an increase more than 5 percent , it is necessary to perform calculation and prove that replacement or alteration is not needed or shall be replaced or altered as needed to carry the gravity loads required by the IBC for new structures.