kbob
Mechanical
- Jan 30, 2004
- 2
I have a hydrotest problem. We have a tubing spec. with a design code of ASME B31.3 designed for a maximum pressure of 15,000 psig. We have successfully hydrotested our system at 22,500 psig. (1.5 times design) for several of our systems. However, one system uses Kalrez seats in the valves. This systems consistently leaks when we exceed 20,000 psig. No permanent damage is done to the system. When we drop the pressure below 20,000 psig the system does not leak. My question is: How can we accept the system as is? I do not see that B31.3 allows us to hydrotest at any pressure other than 1.5 times design.
Other input/ assumbptions:
1. Valves are not welded in place.
2. It seems the code allows reduction in hydrotest pressure when the yield stress is to be exceeded. I assumed this does not apply to the soft goods in the valves.
3. System is a chemical injection pump discharge with a normal operating pressure of 12,500 psig (Set by recycle regulator)
3. Pump discharge PSV set at 15,000 psig.
Any help would be appreciated.
Thanks
Other input/ assumbptions:
1. Valves are not welded in place.
2. It seems the code allows reduction in hydrotest pressure when the yield stress is to be exceeded. I assumed this does not apply to the soft goods in the valves.
3. System is a chemical injection pump discharge with a normal operating pressure of 12,500 psig (Set by recycle regulator)
3. Pump discharge PSV set at 15,000 psig.
Any help would be appreciated.
Thanks