Motors are rated at multiples of 115 volts. (4 x 115V = 460V)
Systems are rated at multiples of 120 volts. (4 x 120V = 480V)
Using 480V as a multiplier rather than 460 gives an allowance for voltage drop between the transformer and the motor.
The 746 W per horse power plus motor losses, plus power factor adjustment, plus voltage drop comes close to 1 KVA per Hp.
From the motor current table in the CEC, and using 480 volts as a multiplier I get the following KVA values for 460 volt rated motors:
50 Hp. 5.4 KVA
100 Hp. 103 KVA
150 Hp. 150 KVA
200 Hp. 199 KVA
Close enough for me.
Years ago I was doing a design for a small shingle mill.
If I bought the transformer and used primary metering I would have to use about 1 KVA per Hp.
If the utility supplied the transformer and we used secondary metering, they would apply a diversity factor and use a factor of 0.5 KVA per Hp.
That was a long time ago, but perhaps some of the utility folk will comment on present practice.