Mbrooke said:
corona ring actually causes corona to get rid of it on the sharp line hardware?
The Corona Ring encircles the hardware that has sharp edges with a Faraday Shield. The outer profile of the Corona Rings have a large effective radius (Thank you for the proof reading David) to lessen or avoid corona.
Rings on insulator strings are grading rings.
Grading Rings should not cause corona. That would be replacing one unwanted effect (Non-linear voltage stresses on the insulator) with another unwanted effect (Excess corona).
A guarding ring or grading rind will generally be round. A corona ring will often be oval or oblong. Other than that, the same considerations for a corona ring such as increased effective radius and smooth surfaces apply to a grading ring.
For example and for visualization: Consider a single conductor suspended from an insulator string employing both Guard Rings and Corona Rings..
The Guard Rings will be horizontal, centred on the ends of the insulator string.
The Corona Rings will be oriented at right angles to the guard rings or vertical and one on each side of the hardware connecting the conductor to the insulator string.
I have been searching with various search engines for several days to find a good picture of Corona Rings.
I came across this which causes me to modify my original explanation somewhat.
[URL unfurl="true" said:
http://tdworld.com/overhead-transmission/corona-rings-are-they-needed[/URL]]
Since 2006, some utilities have been experiencing an increased number of polymer insulator failures on their 115-kV and 138-kV transmission lines. Investigations have shown these failures can be attributed to high electric fields (E-fields) occurring close to, or on the high-voltage end fittings of, these insulators. The findings of the investigations suggest that, contrary to conventional wisdom, it might be necessary to consider the application of corona protection on polymer insulators applied below 161 kV.
A 2008 report by the Electric Power Research Institute (EPRI) was conclusive in its findings that there is an issue with polymer insulator degradation on 115-kV and 138-kV lines on certain configurations and specific insulator designs.
Looking at the results of these fairly recent studies, it seems as though there are instances where the stresses on the ends of the insulators are great enough to cause corona, and the rings serve the dual purpose of both guarding and corona protection.
I apologize for my partly inaccurate information.
I do note the comment in the article:
"The findings of the investigations suggest that, contrary to conventional wisdom, it might be necessary to consider the application of corona protection on polymer insulators applied below 161 kV."
This article seems also to support Mbrooke's comment re: Corona Rings on 138 kV lines.
Never too old to learn. grin
Bill
--------------------
"Why not the best?"
Jimmy Carter