height requirement for receptacle in a kitchen 1

Status
Not open for further replies.

clubhouse

Mechanical
Joined
Dec 4, 2006
Messages
3
Location
CA
what is the maximum height requirement for a residential receptacle for a kitchen counter top.
 
In which country?


----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 
Provinve Ontario, Canada

Cheers
 
CEC Rule #26-710, (k)
Not more than 1.7 meters from the floor.
and
CEC rule #26-712, (d)(ii)
For a free standing gas range, not more than 130 mm from the floor
respectfully
 