Dec 4, 2006 #1 clubhouse Mechanical Joined Dec 4, 2006 Messages 3 Location CA what is the maximum height requirement for a residential receptacle for a kitchen counter top.
Dec 4, 2006 #2 ScottyUK Electrical Joined May 21, 2003 Messages 12,915 Location DE In which country? ---------------------------------- Sometimes I only open my mouth to swap feet... Upvote 0 Downvote
Dec 4, 2006 Thread starter #3 clubhouse Mechanical Joined Dec 4, 2006 Messages 3 Location CA Provinve Ontario, Canada Cheers Upvote 0 Downvote
Dec 4, 2006 1 Moderator #4 waross Electrical Joined Jan 7, 2006 Messages 28,752 Location CA CEC Rule #26-710, (k) Not more than 1.7 meters from the floor. and CEC rule #26-712, (d)(ii) For a free standing gas range, not more than 130 mm from the floor respectfully Upvote 0 Downvote
CEC Rule #26-710, (k) Not more than 1.7 meters from the floor. and CEC rule #26-712, (d)(ii) For a free standing gas range, not more than 130 mm from the floor respectfully