75 - 52 = 23 kW
So, in effect you are having a heating capacity of 23kW inside the room when one unit fails.
You want to know what temperature will occur in the room and how fast temperature will rise.
The temperature that will be reached is given by the equilibrium that is reached when the temperature in the room gets higher than the temperature of the surrounding area (outside?).
At which temperature(-difference) does 23kW "leak" from the room to the surrounding. If this is not outside then the 23kW leaking will also raise the temperature of the adjacent rooms, thus complicating the problem...
How fast the temperature will rise depends on accumulation of heat in various parts making up the room (walls, floors, ceiling, equipment not producing heat itself).
If your equipment room is not very large then 23kW will heat up the volume of air inside the room pretty quickly.
Depending on what temperature is the absolute maximum for the equipment in the room and depending on your local climate it might be possible to keep roomtemperature at a still acceptable level by venting with an appropriate amount of outside air.
Example: max. room temperature 40°C
max. outside temp. 30°C
difference = 10°C
7500 m3/h at 10°C = 25.2 kW cooling