Healthcare facility power system HELP

Status
Not open for further replies.

newtonrolle

Electrical
Joined
Apr 4, 2015
Messages
3
Location
BS
Hello, I have a question regarding Healthcare facility power system, in a clinic, I was told that the code requires me to have another transfer switch, but my interpretation has the system in compliance with NFPA 99. please i would welcome a review and comment of the system. a riser diagram link is attached/in this post.

Thank you
 
 http://files.engineering.com/getfile.aspx?folder=7d5e5cd5-59ec-4387-a1f4-f383ee682548&file=WEST_END_CLINIC_ELECTRICAL_JULY_1ST_2016.pdf
NFPA 70 (NEC) 517.30(B)2 requires it if the demand load is more than 150 KVA.
 
Thanks, If we have a 100% standby generator that can accommodate the clinic's full load, do we still need to separate the essential service from the normal or could we use 1 ATS and 1 main distribution panel with separate sub-panels.the way i read the code that would be acceptable, only if you don't have 100% backup then you just have the normal line with essential on the ATS.

please any advice would be welcome.

Thank you,
 
You can use one ATS and a main distribution panel.

You will need to provide emergency power to any required emergency egress lighting, fire alarm, etc. from independent sources, like batteries.
 
Thank you Peon7, can you take a look at the attached riser and give a quick review.
 
Would you like fries with that?
 