Jul 27, 2012 #1 glenn0123 Mechanical Joined Jun 20, 2012 Messages 6 Location SG Hi guys, I would like to ask if an H beam structure EN10025 S355JR would be applicable for -20deg C or lower temperature area? Thank you very much.
Hi guys, I would like to ask if an H beam structure EN10025 S355JR would be applicable for -20deg C or lower temperature area? Thank you very much.
Jul 27, 2012 1 #2 SJones Petroleum Joined Apr 22, 2001 Messages 3,943 Location GB The R stands for 'room temperature impact values'. It would have to be J2 for -20 deg C. Steve Jones Materials & Corrosion Engineer http://www.linkedin.com/pub/8/83b/b04 Upvote 0 Downvote
The R stands for 'room temperature impact values'. It would have to be J2 for -20 deg C. Steve Jones Materials & Corrosion Engineer http://www.linkedin.com/pub/8/83b/b04
Jul 27, 2012 Thread starter #3 glenn0123 Mechanical Joined Jun 20, 2012 Messages 6 Location SG hi steve, Thank you for your reply I would just like to clarify, does it means that this values from the impact test temperatures will define which temperature I can build or use a certain structure? Upvote 0 Downvote
hi steve, Thank you for your reply I would just like to clarify, does it means that this values from the impact test temperatures will define which temperature I can build or use a certain structure?
Jul 27, 2012 #4 desertfox Mechanical Joined Dec 29, 2002 Messages 5,559 Location GB Hi This link might be useful:- http://steelmanager.eu/files/en10025.pdf Upvote 0 Downvote