Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Generator voltages

Status
Not open for further replies.

bibi1964

Electrical
Joined
Oct 27, 2017
Messages
12
Location
IL
hi

a friend asked me a question:
In the generator test, the voltage between phase and zero was measured
400,400,230
What could be the problem?

thanks
 
It seems Blue phase terminal and star point (neutral terminal) got interchanged it looks.
It could be in the generator terminal box.

Rompicherla Raghunath
 
Operator error.
A-B = 400 Volts
A-C = 400 Volts
A-N = 230 Volts.
The tester inadvertently interchanged one phase and the wye point when testing.
Instead of testing from neutral to A, B, and C he tested from A to B, C, and neutral.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
hi
Further to the question I asked:
Regarding to the attach drawing if I change the connection between points 9 and 12 this mean the star point (4,8,9)
What tensions will I measure between the phases and and neutral
L1-N
L2-N
L3-N

thanks
 
 http://files.engineering.com/getfile.aspx?folder=e86523fd-b30e-46da-b7cb-7ef31875f558&file=v1-09_Section_07_Generator.pdf
Tiredly, 230 V, 230 V and 230 V.
Se my previous post.
To see 400 Volts you are measuring phase to phase. A-B, and A-C. To see 400 Volts from two 230 Volt windings the phase angles are correct.
Your friend had one phase interchanged with the neutral when he took his measurement.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top