The provisions of Chapter for of the UBC or in my case the California Building code, indicate that a high rise building includes all buildings with a habitable floor more than 75' above the lowest exit discharge level that provides fire personnel entry and communication with the rest of the building. With specific exceptions for parking garages, grain elevators, steeples,jails, etc....
A hotel which might have a first floor of perhaps as much as 18' floor-to-floor height for the lobby floor and 13' to 14' floor-to-floor heights for the remainder, may still not be a high rise by Building Code definitions. However, we have a local municipality near here in Riverside, Ca. which has a local ordinance deeming any structure more than TWO stories high as being a high rise structure. So as with all things code, check with the local AHJ before proceeding with the design.
The only copy I have here of the IBC is an old 2000 version, but it states:
SECTION 403 HIGH RISE BUILDINGS
Section 403.1 "Applicability-The provisions of this section shall apply to buildings having occupied floors located more than 75 feet, (22 860 mm), above the lowest level of fire department vehicle access."
Again there are several exceptions listed for airports, parking garages, hazardous occupancies, etc....
Best of luck,
EEJaime