gte447f
Structural
- Dec 1, 2008
- 815
Does a foundation for a 2 MW Caterpillar 3516C generator (80 kips operating weight) need to be analyzed for dynamic effects if it is going to mounted on spring isolators, or do the isolators effectively eliminate concerns about vibration/dynamic loads to the foundation (and the adjacent building)?
What about without spring isolators? Do these generators produce significant vibration/dynamic loads or are the loads negligible? Some say modern engines with an even number of cylinders are "balanced" and so the dynamic forces are negligible.
I have requested dynamic load information from the vendor, but they say the information is not readily available, and that the foundations are routinely designed when they provide only the static loads. They did provide a Caterpillar Installation Guide that basically discounts vibration as a concern. It says,
"Massive concrete foundations are unnecessary for modern multicylinder medium speed generator sets. Avoid excessively thick, heavy bases to minimize subfloor or soil loading. Bases should be only thick enough to prevent deflection and torque reaction, while retaining sufficient surface area for support."
The Installation Guide goes on to suggest sizing the depth of the foundation so that the weight of the foundation equals the weight of the generator (not 3-5 times the weight that used to be frequently quoted as a rule of thumb).
So is vibration not an issue with these machines?
Input from anyone with experience with these types of installations is much appreciated.
What about without spring isolators? Do these generators produce significant vibration/dynamic loads or are the loads negligible? Some say modern engines with an even number of cylinders are "balanced" and so the dynamic forces are negligible.
I have requested dynamic load information from the vendor, but they say the information is not readily available, and that the foundations are routinely designed when they provide only the static loads. They did provide a Caterpillar Installation Guide that basically discounts vibration as a concern. It says,
"Massive concrete foundations are unnecessary for modern multicylinder medium speed generator sets. Avoid excessively thick, heavy bases to minimize subfloor or soil loading. Bases should be only thick enough to prevent deflection and torque reaction, while retaining sufficient surface area for support."
The Installation Guide goes on to suggest sizing the depth of the foundation so that the weight of the foundation equals the weight of the generator (not 3-5 times the weight that used to be frequently quoted as a rule of thumb).
So is vibration not an issue with these machines?
Input from anyone with experience with these types of installations is much appreciated.