Generator Core Iron Problem
wbd
659
We had an insulation failure on a hydro turbine generator. It was sent out for rewind and I am being told that the core iron is bad. They tested 3 times and still havve poor results. I am being told that the temperature is not stabilizing and this not uncommon for old generators with wavy iron. It is a 1905 generator.
1. What is meant by wavy iron?
2. I have a copy of the Stator Core Test sheet. Does anybody know of a primer or resource on what the tests are and how to interpet?
Thank you in advance for any and all replies.
wbd
Unable to see your test sheet. In my opinion, that core is a centurion ready to be retired.
Those days they used hot-rolled magnetic sheets which had greater thickness variation than that of today's cold rolled sheets.
So, when you stack a core with a big bore, like hydro machines, you will see at the back of the core, the stacked core will appear wavy.
I would strongly recommend replacing the core with new cold rolled, non-grain oriented sheets, which have significantly lower losses.
* Women are like the police. They can have all the evidence in the world and yet they still want a confession - Chris Rock *
wbd,
I didn't have the luxury of handling century-old electrical equipment but a parallel experience looks the same as your present problem! I have the same problem with a motor that exhibited higher than normal no-load current drawn. We analyzed the problem and came to a conclusion that the culprit is the core of the stator. We had that motor core re-stacked and the problem was gone.
hope this helps.