If you don't mind I will guess at how the normal system could be used to roll on the IVs.
As stated the CV reference and IV reference are ganged together, in fact they are same value, the CV reference is summed with a set 100% bias to derive the IV reference. a 0% CV reference will will have the IV's 100% open, and a -30% CV reference will have the IV's at 0% open.
Thus set the CV referance to -30% and speed error will control the IVs near 0% open to roll the unit. once "at set speed" rated, the CV referance will be increased, increasing the IV referencae to synch and load the unit. as the IVs open and increase load, the CV referance will be approaching 0%, once IVs are at 100%, the CVs will be opening and continue to increase load.
That would be my guess.
Sounds like an interesting system, much more so than the straight forward speed control units I put into service 20 years ago.