Galvanized steel elbow protection from concrete

Status
Not open for further replies.

eatapeach

Military
Jun 20, 2013
78
Per the 2014 NEC 344.10 4 (B) Galvanized steel may be used in concrete where protected by corrosion. Is the galvanize not the protection for the steel? Are you still required to protect the elbow with an additional layer of protection such as tape?
 
Replies continue below

Recommended for you

Could chromate passivation be what they're looking for here? See this thread:

Dan - Owner
Footwell%20Animation%20Tiny.gif
 
Yes even galvanized conduit will corrode at the interface of the concrete and air. It can be wrapped. We used to use PVC-coated RGS conduit for these.
 