Jan 29, 2021 #1 eatapeach Military Joined Jun 20, 2013 Messages 84 Location US Per the 2014 NEC 344.10 4 (B) Galvanized steel may be used in concrete where protected by corrosion. Is the galvanize not the protection for the steel? Are you still required to protect the elbow with an additional layer of protection such as tape?
Per the 2014 NEC 344.10 4 (B) Galvanized steel may be used in concrete where protected by corrosion. Is the galvanize not the protection for the steel? Are you still required to protect the elbow with an additional layer of protection such as tape?
Jan 29, 2021 #2 MacGyverS2000 Electrical Joined Dec 22, 2003 Messages 8,504 Location US Could chromate passivation be what they're looking for here? See this thread: https://www.eng-tips.com/viewthread.cfm?qid=15644 Dan - Owner http://www.Hi-TecDesigns.com Upvote 0 Downvote
Could chromate passivation be what they're looking for here? See this thread: https://www.eng-tips.com/viewthread.cfm?qid=15644 Dan - Owner http://www.Hi-TecDesigns.com
Jan 29, 2021 #3 dpc Electrical Joined Jan 7, 2002 Messages 8,735 Location US Yes even galvanized conduit will corrode at the interface of the concrete and air. It can be wrapped. We used to use PVC-coated RGS conduit for these. Upvote 0 Downvote
Yes even galvanized conduit will corrode at the interface of the concrete and air. It can be wrapped. We used to use PVC-coated RGS conduit for these.