stillfan
I was hoping soemeone could point me in the direction of where in ASHRAE does it dictate free air space requirment calculations. I ran the calcs for CFM but the client wishes to install a passive system. So the CFM calc means nothing, right?
CFM = Volume *3/60 (3ACH/60min/hr) = 80CFM
What is free air space, or, rather, what do you mean by it?
He is probably thinking about natural air circulation which can also be expressed in CFM.
She - and yes, I am speaking of a passive/ natural air system. When I size my intake and exhaust louvers for a passive system it only uses free air specs so I need to calculate my req free area based on the ASHRAE code.
For example, on a residential crawlspace you have to meet a min req free air vent. You also have to meet these requirements in the attic area.
Does anyone know where I would look for these requirements.
Natural Ventilation is discussed in the ASHRAE Handbook, Fundamentals Volume, Chapter 16.
Do you mean the free, or effective area of the louvre? A natural vent calculation will provide the size of an open hole. When you put a grille in the hole, it blocks a given amount of the space. Any grille/louvre manufacturer will provide the free area of the grille product expressed as a percentage.