Hi All
I have a noob question regarding the definition of 'functional unit' with respect to IEC 60439 (and the new IEC 61439) and there are other equivalent standards over the world.
The standards define a functional unit generically as whatever is between the busbar and the outgoing terminals... does this include VFDs? Soft starters? Contactors? Or is it a generally acceptable interpretation that it just applies to switchgear?
Considering the reason for MCC segregation, i.e. limiting the propagating affects of arcing faults, ease of maintenance and continuity of supply and/or production, I don't see why a VFD or soft starter should not be included in the functional unit. But most of the panels I have seen that claim to be form 3 or form 4 provide segregation between the feeder circuit breakers but do not provide the same for the drives (if present)
Thanks
I have a noob question regarding the definition of 'functional unit' with respect to IEC 60439 (and the new IEC 61439) and there are other equivalent standards over the world.
The standards define a functional unit generically as whatever is between the busbar and the outgoing terminals... does this include VFDs? Soft starters? Contactors? Or is it a generally acceptable interpretation that it just applies to switchgear?
Considering the reason for MCC segregation, i.e. limiting the propagating affects of arcing faults, ease of maintenance and continuity of supply and/or production, I don't see why a VFD or soft starter should not be included in the functional unit. But most of the panels I have seen that claim to be form 3 or form 4 provide segregation between the feeder circuit breakers but do not provide the same for the drives (if present)
Thanks