Histor (Electrical)(OP)24 Sep 24 08:56
'..Is this wiring to Power meter is acceptable as per IEC? We have metering CT installed on upstream of MCCB and connected to power meter. Generally we install CT on Downstream of MCCB. So I got confused if it is acceptable as per IEC'.
I have the following opinion for your consideration,
1. IEC recommendations are for "Safety" use of electricity. It does NOT interferes with the local practice, which are "safe".
2. Technically, both either CTs placed upstream or downstream of the CB are "safe" and measures/reads "correctly".
3. In some locations:
a) the utility's CT are located upstream of the CB in a compartment with sealed door; to prevent any accesses/tampering with by the consumer.
b) if the power (kW) or energy (kWh) meter and CTs are private/owner property, the CTs and voltage are usually taken downstream of the CB. Any rectification works can be done by switching off the CB.
Che Kuan Yau (Singapore)