ITHW, respectfully I disagree with you.
IBC (2000) does not specify any ADDITIONAL safety factor for overturning checks. You simply follow the load combinations.
For seismic - see 1617.4.5. This simply refers to overturning moments at each story based upon Fi at each level. You still use the various combinations, plugging in Fi as QE in section 1617.1.1 along with the vertical seismic component of .2SDSD and you have E to use in the combinations.
For wind, see 1609.1.3 for overturning. Again, no mention of any required 1.5 safety factor. Simply use a slightly underestimated dead load and use within the combinations - specifically 0.6D + W. For the alternative load combinations of 1605.3.2, they require you to use 0.67D instead of D within the load combinations.
If you have any specific code reference mandating an additional 1.5 safety factor, I'd love to be shown, but I'm not aware of any in the current codes.
The commentary for ASCE 7-02, section 2, states: [red]"Load combinations (7) and (8) [these are the .6D+W combos] were new to the 1998 edition of ASCE 7. They address the situation in which the effects of lateral or uplift forces counteract the effect of gravity loads. This eliminates an inconsistency in the treatment of counteracting loads in allowable stress design and strength design, and emphasizes the importance of checking stability."[/red]
There used to be confusion between strength and ASD because of the traditional 1.5 safety factor. i.e. how do you utilized a 1.5 factor for OT with factored loads? This was removed in the recent codes and instead, was included in the load combinations.