jeffhed,
The way your company designs a foundation IMO is the way it should be done in that critical calculations and the foundation design is done by qualified engineers familiar with local regulations. As you found out the technical help at some of the equipment suppliers is limited, and in fact even the D, L, W, and E loads should be of suspect.
aggman,
I like your way of tabulating foundation loads. About a month ago I started working on a new format for our loads drawing similar to what you are doing. As you said it can look like a lot of information in particular when there are moments on base plates. For bins and silos I don't consider 0.6D+0.7E because it seldom controls. That would be another 8 load combinations and I already have 30 or more. I suppose for lighter equipment like conveyors the dead load only might be relevant.
I agree that this is an interesting business being an equipment supplier and working with other suppliers, and after working in it for many years it is my opinion that from the technical standpoint it has gotten worse, not better. But that's probably a better topic for another discussion.
-Mike