Floor Plate with Wheel Load - Sanity Check

Status
Not open for further replies.

CTW

Structural
May 30, 2002
312
I've used Roark's in the past for floor plates with relatively short spans and felt comfortable with the outcome. However, I could use a sanity check for the floor plate outlined below.

The plate is 20 ft wide with a 10.2 ft span. Simply supported along the 20 ft edges only. The applied axle load is 32 kips and the spacing between wheels on the axle is 6 ft. Using the method in Roark for determining the effective width of the plate, I get the following.

b = 20 ft
a = 10.2 ft
b/a = 1.96 (say 2)
e/a = 0.656 (for c=0)
e = 0.656 x 10.2 ft = 6.69 ft

Assuming a 2 inch thick plate
P = 32 kips/2 = 16 kips
I = 6.69 ft x 12 in/ft x (2^3)/12 = 53.52 in^4
E = 29000/(1-0.3^2) = 31860 ksi
L = 10.2 ft = 122.4 in
Deflection = (P x L^3)/48EI = 0.36 inches

I know the numbers say the deflection is 0.36 inches, but it doesn't seem practical. I would have expected the deflection to be much greater with a 16 kip concentrated load applied to a 10.2 ft span, 6.69 ft effective width and 2 inch thick plate. I realize the deflection will be a little larger since the effective widths under each wheel overlap each other, but it still doesn't seem right.

I'm interested in other opinions of this.
 
Replies continue below

Recommended for you

Perhaps an effective width of 6' would be more realistic provided that a wheel does not come closer than 3' from the end. If one wheel is closer to the end than 3', deflections will be higher.

A 10' x 20' x 2" plate sounds a bit extreme. Couldn't you use a few beams and a thinner plate?

BA
 
Thanks BA. That's exactly my point. A 10' x 20' x 2" plate does sound a bit extreme. The original plan was to use a stiffened plate but I was just curious what thickness of plate would be required to span that distance. I guess I'll research to find out if there has been any real world testing of plates based on the equations in Roark. I just can't believe that a 16 kip load is only going to deflect that plate about 3/8".
 
i guess i'm alittle confised with your calc ... PL^3/48EI is for a centrally applied load, no? haven't you got a beam (plate) 10.2' wide with two 16 kips loads applied 6' apart ?

Quando Omni Flunkus Moritati
 
I believe the two point loads act along the 20' length and therefore could theoretically be looked at individually
 