Yep, there are definitely pressures to come up with very fast clearing to minimize ground grid costs. We're working on a number of projects, some with 115kV ground faults approaching 30kA and the clearing time questions get intense. For one project we found that speeding up the remote clearing saved enough ground grid cost to pay for adding breaker failure protection at the remote end.
The pessimistic Protection Engineer wants to consider failure of lots of breakers, say a battery failure. The project manager looks at that cost and pushes back. Ultimately the company has to decide how many contingencies to build the ground grid to contend with and then figure out which collection of those contingencies produces the worst case. That's highly likely to include breaker failure at the remote end of the strongest source.
With ground distance you pretty much know what the remote zone 2 time will be. If all of the remote zone 2 times are the same the worst will be the strongest. But with directional ground overcurrent at the remote ends the remote clearing times vary from line to line and from system configuration to system configuration; a lower current but slower clearing source can be worse than a higher current and faster clearing source.
Ultimately you're weighing the balance and determining that you'll build a ground grid for a really bad event, but not for a terribly horrible event. (Terribly horrible would be at least as bad as no local clearing, no transfer trip, and breaker failure at all remote ends.)