Expansion Joint Location-1 story steel braced frame
Astructengr
I have a 1 story, steel braced frame building. Overall dimensions are 385' by 140'. There are (2) 18'x30' corridors that connect the different wings of the facility. Should those corridors be separated from the main wings by expansion joints? If so, would it be advisable to connect the corridor framing with slotted holes in the east-west direction but tie into the main diaphragm in the north-south direction? There is little room for a moment frame in the north-south direction as the corridors are mostly glass and column depth is limited to 6" in that direction.
I know you can usually go up to 400' in a steel building without expansion joints, but that assumes a mostly rectangular building.
 https://files.engineering.com/getfile.aspx?folder=595d0617-5333-48ed-bd5d-61211bdb110d&file=Expansion_Joint-1_Story_Steel-Braced_Frame.pdf
I'd likely isolate the 'middle' building. Each end is fairly rigid and the juncture of the middle part makes a good joint location. I'd use two joints.
I'd provide two EJ's with slotted holes in E-W direction. One at the right of left corridor, the other at the left of right corridor.
Say my opinion only..
He is like a man building a house, who dug deep and laid the foundation on the rock. And when the flood arose, the stream beat vehemently against that house, and could not shake it, for it was founded on the rock..
Luke 6:48
Thanks everyone! Isolating the "middle" building with(2) joints seems to be the correct solution.