@jdgengineer - Ref ASCE 7-05 commentary - Brief power interruptions and loss of heat are acknowledged in the Ct = 1.0 category. Consequently, heated structures need not be designed for this unlikely event. Some dwellings are not used in the winter. Although their thermal factor may increase to 1.2 at that time, they are unoccupied, so their importance factor reduces to 0.8. The net effect is to require the same design as for a heated, occupied dwelling.
@shobroco: I acknowledge your experience and observations, however,.....
For snow loadings, the American code uses Canadian code as a point of reference for thermal, aerodynamics effects etc. As per ASCE commentary : The combined consideration of exposure and thermal conditions generates ground-to-roof factors that range from a low of 0.49 to a high of 1.01....., all regardless of their thermal condition.
I have worked in Ontario Canada on projects related to pharmaceutical industry. This is what we have done - for new projects full snow load on the units; for checking adequacy of existing members, we started with full snow load on the units, reduced on few occasions, but never less than 2/3 of the roof snow load.
I agree with you, these are subjective.