njg33
Mechanical
- Mar 8, 2007
- 2
We typically size our loads based on 75Deg F 50%RH return air. We have a project requiring 20,000 BTUH sensible cooling for 86 DegF 50%RH air. Most AC system design is based on approx. 45 DegF evaporating temp. How does this now equate with the 86 deg return air?
My understanding is the evap temp will be in the area of 55 degF. However, this is the outer operating limit of our compressor performance.
Can this load be "translated" to a different coil/compressor selection to reduce the evap temperature and run the compressor in a more common operating point? I have always thought the evap temp is a function of the return air temp?
Do I simply run the coil data software at 86 entering temp and 45 deg evaporating and select a compressor to match the cooling load at this evaporating temperature?
Regards,
NJG
My understanding is the evap temp will be in the area of 55 degF. However, this is the outer operating limit of our compressor performance.
Can this load be "translated" to a different coil/compressor selection to reduce the evap temperature and run the compressor in a more common operating point? I have always thought the evap temp is a function of the return air temp?
Do I simply run the coil data software at 86 entering temp and 45 deg evaporating and select a compressor to match the cooling load at this evaporating temperature?
Regards,
NJG