Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Erratical Results Of ETABS in Longitudual Reinforcements

Status
Not open for further replies.

CivilTanju

Structural
May 2, 2006
33
hi all,

yesterday I have encountered a very strange outputs of etabs. I was analysing single storey structure, load case was only with gravity uniform loads on floors (rigid diaphragm), everything went so normal run the analysis and after that i run the design/check( concrete frame,EuroCode-2) i get some longitudual reinforcement outputs for columns on the screen thinking that these are normal results program supposed to create. Then I added some additional(4) storeys on top of the ground floor (load case and code was same). But even now the structure was comprised of 5 floor, the longitudual reinforcement was same with last result on the ground floor columns.

It made me think that longitudual reinforcement is provided only with min percentage specified on code(Eurocode-2) as long as concrete cross section bears all the axial-load capacity.

Any idea??


Best Regards,
 
Replies continue below

Recommended for you

Of course, you set the min & max value for the percentage of reniforcement.

Pls change the min value to 0.001 and check the steel requirement.

Hope this helps

Cheers
 
you need to check the min values for column. If that is not being exceeded your output will not change. try reducing column size.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor