Further to your other replies, an Engineer can estimate in a long run of pipeline (ie distribution networks) by adding 10% to the measured length, due to the long lengths and minimal fittings. However for pipework which in small lengths could have numerous fittings and therefore a range of 50 - 100% additions should be added. The above will get an estimated effectiove length (EEL), to get a True Effective Length (TEL) one would then go to relevant tables for K and zeta values for each type of fitting which can be time consuming if doing manually. CIBSE Volume C has a table and diagrams for fittings etc, it depends how accurate you want to be to that end manufacturers will have the more accurate data.
in addition careful thought must be applied as tables etc tend to oversize pipework, useage must be researched as infrequenbt use can lead to Legionella as hot and cold water systems are the main causes as air conditioning systems have this issue controlled due to maintenance regimes.