Emergency panel in Hazardous area 1

Status
Not open for further replies.

Jed057

Electrical
Joined
Mar 18, 2009
Messages
35
anyone can give me the answer.

Regarding Lighting panel was located in hazardous area and TNS system need 3 phase + N ,my question related to all power incomer cable need to have switch for cut neutral cable or not,
If switch incomer only 3 Pole and no switch at nutral ,Is it dangerous ?
 
Jed057,
Any 3 Ph. electrical feeder that supplies a load situated in a hazardous area shall be equipped with a 4 poles switching device.
This is to mitigate the hazard that may appear due to accidental existence of potential difference between neutral and earth, which can represent a source of ignition (i.e. a spark capable to ignite the flammable surrounding atmosphere).




 