eamonkerrigan
Electrical
- Jan 5, 2007
- 17
I am having a hard time finding information about nuetral grounding reactors. Hopefully you can help me with a few issues.
I'm replacing two 10/12.5 MVA auto-transformers with one 15/20/25MVA Delta-Zigzag. Voltage is 23-13.8kV. Planning needs a really low impedance on XFMR(2.18%) which is making my ground fault currents really high. So I need a neutral reactor to compensate.
We don't have a spec so I'm trying to develop one based off of our CLR reactor spec.
However, it seems to me that C57.16 does not apply to neutral reactors (correct me if I am wrong).
It seems like neutral reactors fall under C62.92 which is neutral grounding in Utility Systems. However, there is very little talk about reactors (except for generators which I am not!)
There is also IEEE32, but again neutral reactors are barely a footnote.
My big questions are:
-BIL...Do I just calculate the voltage drop accross reactor? or do I match the XFMR nuetral BIL?
-No requirements about dielectric ratings in any standard I can find. It is very important for CLR's but not for neutral reactors?
-Continuous current rating (IEEE32 seems to say percentage of thermal current rating?)
-Finally, a real stumper. There is a note in IEEE32 which states third harmonic current shall not exceed 15% of rated continuous current. I know I have a lot of 3rd harmonics (that's actually why we're putting in the delta-zigzag), so should this drive my continous current rating? I don't know where this requirement is coming from? Thermal issue?
I'm replacing two 10/12.5 MVA auto-transformers with one 15/20/25MVA Delta-Zigzag. Voltage is 23-13.8kV. Planning needs a really low impedance on XFMR(2.18%) which is making my ground fault currents really high. So I need a neutral reactor to compensate.
We don't have a spec so I'm trying to develop one based off of our CLR reactor spec.
However, it seems to me that C57.16 does not apply to neutral reactors (correct me if I am wrong).
It seems like neutral reactors fall under C62.92 which is neutral grounding in Utility Systems. However, there is very little talk about reactors (except for generators which I am not!)
There is also IEEE32, but again neutral reactors are barely a footnote.
My big questions are:
-BIL...Do I just calculate the voltage drop accross reactor? or do I match the XFMR nuetral BIL?
-No requirements about dielectric ratings in any standard I can find. It is very important for CLR's but not for neutral reactors?
-Continuous current rating (IEEE32 seems to say percentage of thermal current rating?)
-Finally, a real stumper. There is a note in IEEE32 which states third harmonic current shall not exceed 15% of rated continuous current. I know I have a lot of 3rd harmonics (that's actually why we're putting in the delta-zigzag), so should this drive my continous current rating? I don't know where this requirement is coming from? Thermal issue?