Distribution Power Transformer Neutral Grounding Reactor

Status
Not open for further replies.

eamonkerrigan

Electrical
Jan 5, 2007
17
I am having a hard time finding information about nuetral grounding reactors. Hopefully you can help me with a few issues.

I'm replacing two 10/12.5 MVA auto-transformers with one 15/20/25MVA Delta-Zigzag. Voltage is 23-13.8kV. Planning needs a really low impedance on XFMR(2.18%) which is making my ground fault currents really high. So I need a neutral reactor to compensate.

We don't have a spec so I'm trying to develop one based off of our CLR reactor spec.

However, it seems to me that C57.16 does not apply to neutral reactors (correct me if I am wrong).

It seems like neutral reactors fall under C62.92 which is neutral grounding in Utility Systems. However, there is very little talk about reactors (except for generators which I am not!)

There is also IEEE32, but again neutral reactors are barely a footnote.

My big questions are:
-BIL...Do I just calculate the voltage drop accross reactor? or do I match the XFMR nuetral BIL?
-No requirements about dielectric ratings in any standard I can find. It is very important for CLR's but not for neutral reactors?
-Continuous current rating (IEEE32 seems to say percentage of thermal current rating?)
-Finally, a real stumper. There is a note in IEEE32 which states third harmonic current shall not exceed 15% of rated continuous current. I know I have a lot of 3rd harmonics (that's actually why we're putting in the delta-zigzag), so should this drive my continous current rating? I don't know where this requirement is coming from? Thermal issue?
 
Replies continue below

Recommended for you

IEEE32 is the only one which covers Neutral Grounding reactors. The continuous current rating is just a way of ensuring that the reactor can meet the short time current. For a 10 second time IEEE32 states a continuous rating of 3%.Your Spec needs to state the short time ground current, and the length of time. A company which makes neutral grounding reactors can take it from there. Typically the reactors do not have a continuous current.
 
1- I suggest IEEE Std 142-1991). IEEE Recommended Practice for Grounding of Industrial and Commercial Power Systems.
By IEEE Std-142-1991 reactor shall be sized for a minimum ground fault current of 25%
and prefer 60% of three-phase fault current , for avoiding hard transients overvoltages. It refers to 3 < X0/X1 < 10.
2- You should use neutral BIL of zigzag transformer grounded with X0/X1> 3.
3- Technical Caracteristics:
- rated whitstand voltage at industrial frequency
- rated whitstand voltage at lightning impulse
- Indutance (in mH)
- Current (through fault)
- duration of current (10 s.)
4- You should made all calculation of impedance in ohms.
After that you convert to indutance units.
Is is convenient to check with manufacture about dimensions of indutance coil.
 