As always, it depends. Where are the two sources located? If they are both local transformers, the current will all flow to the Main A transformer neutral through the ground grid. If the sources are from the same remote substation, some of the return current will flow through the earth to the remote substation, some will flow through each of the shield wire/neutral to the remote substation. If the sources are different remote substations, some current will flow through the earth to remote substation A, some will flow through the Main A shield/neutral to remote substation A, some will flow through the Main B shield/neutral to remote substation B, then through the Substation B ground grid and earth to remote substation A, some will flow through tower grounds of Main B and then to the remote substation A ground grid.