SilverArc
Electrical
- Sep 20, 2006
- 82
Hi Everybody,
I have made sure, that I am not asking a question that has been answered before.
I had no doubts earlier about this problem before I spoke to few manufacturers.
The application is a 4160 V 1250 HP Dewatering pump operating power factor .86.
It is started using Direct on line starter, using a Vacuum Contractor. The idea is to connect this medium voltage cap. bank.
As per my information, Cap Banks are of two types; Fixed or Switched. Typically Switched will be an automatic cap bank using some kind of controller.
I called a sales guy from Eaton and he advised that In medium voltage, you cannot connect a 600 KVAR cap. bank right away, because that will create issues of over voltage. So, the best way to avoid is using a CT to measure current and inject 150 KVAR cap bank in sets of four. This CT will activate a controller that will insert each set bank.
He also mentioned some Code regulation and some IEEE standard.
The I spoke to a Engineer rather a Sr. Engineer from GE, who has been involved in starting of 20 MW motors using 10-12 MVAR cap banks. He did not outwardly reject the sales guy idea but advised that you might have to worry about some issues like, when you insert the cap bank after the Contactor before motor, It might lead to over excitation when the power supply is off.
I tried to understand this issue using ETAP and did a motor starting analysis but it did not create any over voltage.So, that was not done the right way.
I tried to understand that phenomena theoritically in a transient fashion: Here are my arguments;
When the motor start, the first thing is Inrush for one cycle or so and then the starting current for 2 secs, In the mean time motor gains speed. How do we account for the Inrush current of capacitor banks.
This was my Story.
Basically, I need advise from people who have used medium voltage capacitor banks for medium voltage motors with Direct on line starting.
Thanks
I have made sure, that I am not asking a question that has been answered before.
I had no doubts earlier about this problem before I spoke to few manufacturers.
The application is a 4160 V 1250 HP Dewatering pump operating power factor .86.
It is started using Direct on line starter, using a Vacuum Contractor. The idea is to connect this medium voltage cap. bank.
As per my information, Cap Banks are of two types; Fixed or Switched. Typically Switched will be an automatic cap bank using some kind of controller.
I called a sales guy from Eaton and he advised that In medium voltage, you cannot connect a 600 KVAR cap. bank right away, because that will create issues of over voltage. So, the best way to avoid is using a CT to measure current and inject 150 KVAR cap bank in sets of four. This CT will activate a controller that will insert each set bank.
He also mentioned some Code regulation and some IEEE standard.
The I spoke to a Engineer rather a Sr. Engineer from GE, who has been involved in starting of 20 MW motors using 10-12 MVAR cap banks. He did not outwardly reject the sales guy idea but advised that you might have to worry about some issues like, when you insert the cap bank after the Contactor before motor, It might lead to over excitation when the power supply is off.
I tried to understand this issue using ETAP and did a motor starting analysis but it did not create any over voltage.So, that was not done the right way.
I tried to understand that phenomena theoritically in a transient fashion: Here are my arguments;
When the motor start, the first thing is Inrush for one cycle or so and then the starting current for 2 secs, In the mean time motor gains speed. How do we account for the Inrush current of capacitor banks.
This was my Story.
Basically, I need advise from people who have used medium voltage capacitor banks for medium voltage motors with Direct on line starting.
Thanks