Ok, I done that. You will need to know the soil properties and a lot of other details:
Need the weight of the generator and any significantly heavy harnesses or lifting fixtures.
Need the full specs on the crane including it's lifting capacity, weight, size of the crawler tracks, etc.
Need to know how the generator will be handled by the crane, i.e. what will be the boom angle? will the crane swing while it is holding the load - that will change the load distribution.
The load distribution will NOT be uniform on the crawler tracks - need to make some reasonable assumptions for that.
Is the ground level, or on an incline - if so, how much?
What will be the duration of the load on any given spot? Perhaps a small number of minutes, maybe longer if there are delays.
Need to know the depth and properties of the of utilities (pipeline? direct buried cable? concrete encased electrical duct bank?) Also, need to have a realistic idea of how much settlement, if any, is allowable.
Once you have this info and have made necessary calculation and assumption you should get an idea of expected soil settlement.
IMHO, the best answer to your project is to take steps to minimize settlement. This could include the use of a crane with larger crawler tracks, or the use of (structural, usually wood) mats between the crawlers tracks and the soil. Maybe even a temporary soil surcharge over the path the crane will take.
Sorry, no easy answers... just a lot of assumptions based on engineering judgment and a detailed conservative examination of the entire move.
![[r2d2] [r2d2] [r2d2]](/data/assets/smilies/r2d2.gif)