TORCHMAN
Structural
- Sep 8, 2023
- 70
Good Evening,
I am designing a moment frame for a house and want to run some ideas by you and see how others engineers would approach this. It is an existing house and a proposed addition is being designed. This addition is a great room with a scissor truss. The exterior walls are about 5.5m tall without a mid-floor in this section of the addition. As it concerns the lateral stability, I am not concerned with the one side (north side on the plan) as it meets the existing structure creating stability as it ties to an existing roof and has a mid floor. On the south side, however, it has the tall walls and large openings. With the wood code in my area limiting shear walls to having a height no taller than 3.5 width of the segment of shear wall, none of my walls can be used as shear walls. Plan and Elevation Below
I find the use of moment frame to be the correct approach in this situation. Let me know if you agree. If so, I have modelled as per below. In such case, I am still getting some large deflections but I am not using the wood framing in the model which will help to stiffen this frame. How do you propose I use it in my calculations? Should I use a better software and model it as a plate? Or should I not use it at all?
Columns are HSS 127x127x9.5
Beams are W200x21
I am designing a moment frame for a house and want to run some ideas by you and see how others engineers would approach this. It is an existing house and a proposed addition is being designed. This addition is a great room with a scissor truss. The exterior walls are about 5.5m tall without a mid-floor in this section of the addition. As it concerns the lateral stability, I am not concerned with the one side (north side on the plan) as it meets the existing structure creating stability as it ties to an existing roof and has a mid floor. On the south side, however, it has the tall walls and large openings. With the wood code in my area limiting shear walls to having a height no taller than 3.5 width of the segment of shear wall, none of my walls can be used as shear walls. Plan and Elevation Below


I find the use of moment frame to be the correct approach in this situation. Let me know if you agree. If so, I have modelled as per below. In such case, I am still getting some large deflections but I am not using the wood framing in the model which will help to stiffen this frame. How do you propose I use it in my calculations? Should I use a better software and model it as a plate? Or should I not use it at all?
Columns are HSS 127x127x9.5
Beams are W200x21