gmoney731
- Oct 24, 2018
- 32
I have attached an image "Problem.png" that shows the gusset plate of interest, and the context of the loading. The axial compression load of 10 Kips is applied from the L3x3x1/4 brace to the connection at an angle of 45 degrees.
Problem.png:
I have also attached a PDF that is supplemental for my approach of the weld design.
Based on this image, I came up with several checks for both the plate and the weld:
Gusset Plate
-Check for plate bending (the X component of the angled load multiplied by the eccentricity)- AISC Chapter F
-Check for plate shear (again, the X component of the angled load) - AISC Chapter G
-Check for plate combined axial and flexure - AISC Chapter H
Weld
-Check weld per AISC 14th Design Example Chapter J.2 - fillet weld loaded at an angle, which is essentially based on Chapter J from AISC
-Check weld combined stress capacity using attached "Weld.pdf"
The members are already checked and sized using RAM Elements. Aside from maybe checking the bolted connection itself (bolt shear, bolt bearing), is there anything else I am missing?
Problem.png:
https://files.engineering.com/getfile.aspx?folder=94d15d75-0bc1-4ff9-b199-ff0601d79bbf&file=Weld.pdf
Gusset Plate
Weld