PJC69
Civil/Environmental
- Jul 18, 2005
- 4
I have modelled a residential development for which we are required to attenuate the post development peak discharge to the level of the pre-development peak discharge for all events up to 1 in 25 year storm. The catchment is small (2 Ha) and the time of concentration 10 minutes. I have received back comment from the local authority who do not appear to be familiar with the SCS Methodology of using synthetic 24 hour storms with nested rainfall intensities. They comment ... it appears that the option selected in your programme only shows storage required after 11 hours of precipitation, and it is suggested that this antecedent condition is clearly intended for much larger catchments than your development. It is our experience that the critical storm is likely to be between 20 and 40 minutes duration, and storage volumes in the attenuation pond will be significantly more that Hydrocad calculates using the 24 hour storm.....
Anyone been faced with a similar response from the regulating authority and how did you convince them that the method used is correct ?