I've used avscorreia sheets and a manual calculation accordingly to Paulo Cachim 's "Estruturas de Betão: Bases de Cálculo", which is also based on EC2. Altough the methods don't seem to be similar they provided at least comparable results for a 9.8m beam, but were both very far from the results of the model(more than 10cm in instantaneous deflection. In my opinion this happened because the cantilever slab has 1.5m x 9.8m, and therefore it will work primarily in one direction, making a 2-way analysis pointless. So I will determine the slab height with EC2 (which is kind of a prescritive method, but is applied to slabs, just as ACI does) and take in consideration the multiplication factor of a 1.5m * 1m beam, giving the relatively short cantilever.
But to anyone having this issue::
As of today, between EC2 and Gilbert's work, both provide a way to calculate the deflection of concrete elements taking in consideration creep, shrinkage and the cracking of a 1-way element, but be careful, on EC2 "...Simplified creep factors are used and
deflection from the curvature of the slab is approximated using a factor."
For 2-way slabs you can find some information on page 324 of Gilbert's book, chapter 8.4. However, it's a predictive method (p. 326), so it also must be taken with a grain of salt.
One other source is TR58. This technical report also deals specifically with 2-way slabs and provides several methods, altough I didn't access it, it's briefly refered in a concretecenter.com document (a example is provided in this pdf, but the support conditions are different from a cantilever).
Excuse my bad english, I hope this helps if someone comes across with the same problem.