JohnMcNutt
Industrial
I came across an interesting generator configuration that I would like to run by you guys.
It is a 12.5 kW generator set up to deliver 120v only. The windings are just a regular 12 lead but they are connected as a 120v parallel (low) delta, corner grounded.
The scant documentation I have ever seen on getting 120v out of a 12-lead delta shows the power all connected between the ends of the U winding. The V and W are out-of-phase connected in series across the U winding and presumably carry half the load with the in-phase U winding--right?
Let's label the corners of this delta RST for argument's sake since delta makes this confusing with U1=R=Neutral.
In this installation it appears that they built it so that half the 120v loads are connected R/N - S and half are R/N - T. I don't think there are any loads between S - T.
It seems to me that in this case, spreading loads like this might be counterproductive because if you kept them all connected across the U winding, the current would divide equally across the two current paths, but now that you have moved stuff to half of the alternate current path, the balance would be messed up.
I suppose this would be easy enough to check with an amp-clamp and a load bank if there is enough slack in the leads.
Thanks for looking.
Thanks for looking.