smitty9898
- Dec 8, 2003
- 30
I recently worked on a project where I was asked to develop reinforcing to create an opening in a brick masonry load bearing wall. The opening was approximately 9’ and the cross section of the wall was triple wythe brick masonry. We were looking at using the “pinch beam” method (as found in prior posts), but it was determined that the stresses in the “thru-bolts” were too high.
I’m trying to figure out how other engineers analyze this problem. More specifically, what is the load path?
Here is the load path that I assumed:
1. The vertical dead loads within the triangle above the opening are bearing on the thru bolts. (i.e. the bolts between the steel channel that sandwich the brick masonry.
2. The masonry creates bending and shear stress on the thru bolts which are transmitted to the steel channels on each side of the wall.
3. The concentrated loads from the thru bolts are transmitted to the steel channels by bearing.
4. The loads from the thru bolts create bending and shear stresses on the steel channels which are transmitted to the ends of the steel channel.
5. The loads from the steel channels are supported by thru bolts that are located outside of the opening
6. The loads in the bolts are transmitted to the masonry wall through bearing.
7. Loads in masonry wall are transmitted to the foundation.
Since the “pinch beam” in my situation resists floor live loads on both sides of the wall, the stresses in the thru bolts were high, and were inadequate.
Does anyone assume that the steel channels act compositely with the brick masonry?
I’m trying to obtain other engineer’s opinion on this topic, and how the loads were analyzed.