VYordan
Structural
- Dec 28, 2009
- 15
I designed the deck 8 years ago for a building that has an underground parking level with a roof that is also used as a an open parking deck. The structural system beams run from east to west and are 4'wide x 1.5'deep including the slab. The slab runs north to south traversing the beams with CLEAR spans being 24',20', 25'and 14'. Loading consists of the slab weight (100 psf) and live load (50 psf)
Initially, the system was designed as a one way beam using a frame analysis and design program. The actual reinforcement illustrated on the drawings is twice to three times the required from calculations to take into account impact. Temperature reinforcement was specified as #4@10" bottom. Recently the system was modeled using SAFE and the original design was corroborated. Cracked section analysis was performed and long term deflections were in the order of 0.19" for live loads and lower for the slab weight. The gravity system consists of shear walls running from north to south and a perimeter 8” basement wall under the slab.
Most of the cracks do not run parallel to the beams in midspans which would indicate a flexural problems, -especially for the longer spans- but parallel to the one way slab direction - there are a few parallel cracks –with signs of infiltration- running 7' to 10' from each other. Also what confuses me more is various angled cracks radiating near the beam support in one area of the 25' span. These crack patterns are not explained by the expected response of the slabs to the loads, being a one way system. The crack patterns described are in plan view seen from below. The slab on top is covered by a waterproofing membrane which was not given any maintenance by the owner thru out the years as evidenced by rips in it. Concrete was specified as 5,000 psi with a maximum WCR of 0.5. Reinforcement is A-615. Concrete cylinder tests and submittals during construction confirmed the design parameters. The total surface area is in the order of 80'x100'. Most of the cracks in are in the 24' and 25'spans. Some in the 20' and even 14' spans. Negative reinforcement over beams is #5@5”and positive reinforcement in the 24’and 26’ spans is $5@12”.
I suspect the following: 1. Top & bottom reinf. covers much more than specified. I specified a sloping form to account for the drainage slopes and it looks that the slab bottom is level and the top surface was sloped, probably leaving the top reinforcement as if it was a uniform 8" slab (there are cracks running on top of slab corresponding to the negative moment parallel to the beam support in the 25’span) 2. Actual WCR higher than specified. Recent core tests provided resistances varying from 2,500 to 4,500 psi. 3. Overloading of the slab with concentrated loads during construction with some type of crane loading or some other temporary loading such as concrete block stacking, which might explain the diagonal cracks near supports. 4. Have to check any embedded piping or conduits inside slab, might explain something…. There are some localized circular patterns also with signs of infiltration. NO deflections are apparent. Please also note that the beam supports are so rigid that the slabs behave as if they were single spans fixed at the supports.
Initially, the system was designed as a one way beam using a frame analysis and design program. The actual reinforcement illustrated on the drawings is twice to three times the required from calculations to take into account impact. Temperature reinforcement was specified as #4@10" bottom. Recently the system was modeled using SAFE and the original design was corroborated. Cracked section analysis was performed and long term deflections were in the order of 0.19" for live loads and lower for the slab weight. The gravity system consists of shear walls running from north to south and a perimeter 8” basement wall under the slab.
Most of the cracks do not run parallel to the beams in midspans which would indicate a flexural problems, -especially for the longer spans- but parallel to the one way slab direction - there are a few parallel cracks –with signs of infiltration- running 7' to 10' from each other. Also what confuses me more is various angled cracks radiating near the beam support in one area of the 25' span. These crack patterns are not explained by the expected response of the slabs to the loads, being a one way system. The crack patterns described are in plan view seen from below. The slab on top is covered by a waterproofing membrane which was not given any maintenance by the owner thru out the years as evidenced by rips in it. Concrete was specified as 5,000 psi with a maximum WCR of 0.5. Reinforcement is A-615. Concrete cylinder tests and submittals during construction confirmed the design parameters. The total surface area is in the order of 80'x100'. Most of the cracks in are in the 24' and 25'spans. Some in the 20' and even 14' spans. Negative reinforcement over beams is #5@5”and positive reinforcement in the 24’and 26’ spans is $5@12”.
I suspect the following: 1. Top & bottom reinf. covers much more than specified. I specified a sloping form to account for the drainage slopes and it looks that the slab bottom is level and the top surface was sloped, probably leaving the top reinforcement as if it was a uniform 8" slab (there are cracks running on top of slab corresponding to the negative moment parallel to the beam support in the 25’span) 2. Actual WCR higher than specified. Recent core tests provided resistances varying from 2,500 to 4,500 psi. 3. Overloading of the slab with concentrated loads during construction with some type of crane loading or some other temporary loading such as concrete block stacking, which might explain the diagonal cracks near supports. 4. Have to check any embedded piping or conduits inside slab, might explain something…. There are some localized circular patterns also with signs of infiltration. NO deflections are apparent. Please also note that the beam supports are so rigid that the slabs behave as if they were single spans fixed at the supports.