Cp Calculation for Beam analysis

Status
Not open for further replies.

EntryLevelEIT

Structural
Jun 24, 2010
42
If Lb falls inbetween Lp and Lr the Cb value is required to find the bending moment. Suppose the applied load to the beam is unsymmetric. I have a simple span with an off center point load.
Is the Cb = 12.5M/(2.5M+3Ma+4Mb+3Mc)Rm equation still valid or should I just rely on the AISC available moment charts.

Thanks guys!
 
Replies continue below

Recommended for you

Yes, the equation is still valid. Or, you can always conservatively take Cb=1.0.
 
My Cb value is causing the Mn between Lp<Lb<Lr to be greater than FyZx. How can this be?
 
Slick is right. In fact, every beam limit state has as its upper limit Mn= xxx <= Mp.

What Cb allows you to do is shift the entire LTB moment curve "up", but never beyond the plastic moment capacity.
 