If Lb falls inbetween Lp and Lr the Cb value is required to find the bending moment. Suppose the applied load to the beam is unsymmetric. I have a simple span with an off center point load.
Is the Cb = 12.5M/(2.5M+3Ma+4Mb+3Mc)Rm equation still valid or should I just rely on the AISC available moment charts.

Thanks guys!
 
Yes, the equation is still valid. Or, you can always conservatively take Cb=1.0.
 
My Cb value is causing the Mn between Lp<Lb<Lr to be greater than FyZx. How can this be?
 
You can never use Mn > Mp (FyZx). The upper bound is Mp

 
Slick is right. In fact, every beam limit state has as its upper limit Mn= xxx <= Mp.

What Cb allows you to do is shift the entire LTB moment curve "up", but never beyond the plastic moment capacity.
 