wcaseyharman said:
At 600VAC that's 810VAC - I probably would pick a 1000VDC contactor or thereabouts to handle some potential overvoltage.
Forget the AC rating completely.
I had an adventure with a 600 VAC 10 Amp relay.
600 VAC rated, double break.
Two contact sets were used in series.
That should be good for 1200 VAC, right.
Certainly more than 600 VAC.
The relay was used to control a 110 VDC brake coil on a motor.
Just a couple of Amps at 110 VDC.
The relay arced over all four break points.
With just 2 or 3 Amps, there was no major damage, but the arc persisted.
The arc melted the silver alloy contact faces, which then flowed together and shorted out the circuit.
Once the arc was replaced by molten metal, there was little heat generated and I found the brake energized and four little silver alloy hourglasses bridging the four contact sets.
DC interrupting is much harder than AC interrupting.
Use a DC contactor rated at somewhat above the peak AC voltage, as Wcaseyharman recommends.
Don't even think about trying to convert an AC rating to DC.
--------------------
Ohm's law
Not just a good idea;
It's the LAW!