I recently specified a minimum 225-amp, 3-pole, 240 volt rated electrical contactor for a project. It's function is simply to remove power from a panelboard feeding cooking equipment under a kitchen hood when the hood fire protection system is activated. So there will be very little switching for this contactor. It is an electrically held contactor, constant voltage to the coil. Remove voltage contactor drops out, apply voltage contact closes.
Our client has a problem. Come in kitchen to cook and no power to cooking equipment. This contactor dropped out but there is still voltage to the coil. Turn off control voltage at the circuit breaker then re-apply, contactor re-engages. Ok, long explanation.
Bottom line this contactor has an anti-telegraphing feature that basically keeps the contactor from re-engaging for very short term switching. If there is a short power blip, contactor won't re-engage. I can switch the circuit breaker very quickly and it won't re-engage.
Manufacturer says this is a standard safety feature for their contactors of this size and larger. I've never run into this before. I didn't specify it that way. Is it standard for all manufacturers or is this guy blowing smoke?