PHovnanian,
Thank your for your reply. While the Electrical plans reference SMACNA for seismic and attachment, The SMACNA book (that I have) dosen't get into references regarding attachment....
You asked,
"what is the exact SMACNA requirement for distances from beginning/end of sweep to the required support?"
That is a ELE CODE answer, every 10'.
SMACNA, (from memory, as my book/s are in my office), 'when the pipe, conduit or duct changes directions'.
Which would be at each end of the sweep (approx 12" on a 1" conduit). Or within 18" of a 90* fitting on pipe, or duct.
further....
Regarding this issue, the ele contractor did get a response from the SE on Friday afternoon.
The SE stated, "attachments shall follow SMACNA, NUSIG, or other accepted industry standardized guidelines. It is the Contractors' responsibility to demonstrate compliance with such standards."
I do not have a NUSIG book...someday I suppose I will. I haven't found any free info online that address this as well.
Your thoughts?
Inspector Steve
DSA, OSHPD, Inspector
So. California.