Fiberglass Conduit
lyla1711
Has anyone ever used fiberglass conduit? I'm working on a site with heavily loaded below grade conduit runs with high load factor, and the fiberglass is supposed to help the cable ampacity derating (it does a better job of radiating heat than hdpe or PVC).
I've used the 90s, and they were great to work with, but most of the heavily loaded stuff I see is aerial, so I was hoping to get some feedback on how common this is, whether or not it actually works, or any other relevant experience with this stuff.
According to Neher&McGrath Table VII Constants for Use in Equations 41 and 41(A) [for cables temperature rise in a pipe-duct or conduit- calculations] it is not a big difference between metallic and fiber pipes. However, the thermal resistance [see Table VI Thermal Resistivity of Various Materials] for fiber duct is 480 but for a metallic duct thermal resistance is negligible. So, the temperature rise of a cable in a fiber duct it is more than in a metallic one.
Putting the cables in metal pipe, fiberglass duct, or plastic does nothing to the thermal resistance of the dirt. Duty cycle may be controlling as the dirt has a bunch of thermal inertia. Does Neher&McGrath address duty cycle?
It is very interesting how each part of the heat evacuation way reacts on variable heat load, indeed. All the known cable ampacity calculation standards consider steady state load-as far as I know.
However, in order to provide a good protection of power cables there are standards which present a way to appreciate the maximum permissible overload for different cable installation way and different overload durations as IEEE 242 /2001-chapter 9.5.2 Overload capacity-for instance. So, nor IEEE standards neither IEC standards, as IEEE 835 [according to Neher McGrath theory] or IEC 60287[IEC 60364-5-52 for low voltage and IEC 60502-2 for medium voltage] consider variable load ampacity calculation.
The IEC Standard 60287-1-1 chapter 1.4.2 Buried cables where partial drying-out of the soil occurs presents the calculation in the
case when the soil is drying around a power cable run underground directly buried in the soil. There is different study to state the critical
temperature in different soil type. See -for instance
On-line monitoring device for dry zone formation in the soil surrounding underground power cables.